Column base plate design to EC3

Tekla Structural Designer
2021
Tekla Structural Designer

Column base plate design to EC3

Column Bases: only simple column bases are supported in the current release.

Unless otherwise stated all calculations are in accordance with the relevant sections of EN 1993-1: 2005 (Refs. 1 and 12) and EN 1992-1: 2004 (Ref. 6).

The following advice is written principally from the point of view of operating column base plate design from within Tekla Structural Designer.

Practical applications

In the current release of Tekla Structural Designer only simple column base plate design checks are supported, following design procedures based on SCI P358 (Ref. 11).

Tekla Structural Designer will check the base plate size and thickness, the shear resistance of the base, the size of the foundation bolts, and the size and type of any welds that are required.

Graphics are used to display the base plate in its current state. You can therefore graphically see the base that you are defining and the results that the design process has achieved. This allows you to see the effects of any modifications that you make, instantly on the screen.

Note: simple bases and moment bases adopt quite different design models. You will find that a moment base with a very small moment will not result in the same design as a simple base (zero moment) carrying the same axial load. You should therefore judge whether the moment is negligible for each such design. If it is, you can design a simple base, otherwise a moment base design (in Tekla Connection Designer) will be appropriate.

Scope

Design Code Options

Simple column bases can be designed to the following EC3 code versions:

  • EC3
  • EC3 Finland NA
  • EC3 Ireland NA
  • EC3 Malaysia NA
  • EC3 Norway NA
  • EC3 Singapore NA
  • EC3 Sweden NA
  • EC3 UK NA
Note: There is no EC3 part 8 for Malaysia so EC3 recommended values are used instead.

Base plate steel grades

Base plates will use S235, S275, S355 and S460 family groups. Strengths greater than 460 are beyond scope. User defined grades ≤ 460 are allowed.

Design method and valid sections and forces for design

Base plate design uses the ‘Effective area’ method for axial compression loads, with horizontal major and/or minor shear allowed, but no moments i.e. pinned base design without uplift. Only I/H and hollow section steel columns are valid for design. Minor shear is a valid design force for base plates on all of these column sections except for Rectangular Hollow Sections.

Column position on the base plate

The column can only be concentric on the base plate.

Base plate position on the concrete foundation

The base plate can be eccentric on the concrete foundation along both the minor and major axes. Note, such eccentricities are achieved in the concrete foundation properties.

Concrete foundation design

Concrete foundation design is separate to, but cognizant of, the base plate design. Only isolated foundations are valid concrete foundations for base plate design checks in first release.

Tekla Connection Designer

Under EC head code there is no longer an option to export a base plate to Tekla Connection Designer from Tekla Structural Designer. For EC design checks, of moment bases for example, Tekla Connection Designer can still be used as a standalone product.

Theory and assumptions

Design method

The ‘Effective area’ method is used for design. The principle steps in this method are as follows:

  • Calculate the design bearing strength, fjd

  • Calculate the required plate area, Areqd and the actual area provided, Aplate

  • Compare Aplate and Areqd (Note, Aplate must be greater than Areqd to proceed)

  • Calculate the stiff cantilever projection dimension, ‘c’

  • Calculate the effective plate area, Aeff

  • Compare Aeff and Areqd (Note, Aeff must be greater than Areqd to ‘pass’)

Clarification of the design bearing strength calculation

The design bearing strength, fjd, between the underside of the base plate and the bedding material in the grout space is given by:

fjd = βj * α * fcd

Where

βj = foundation joint material coefficient = (2/3)

α = a coefficient which accounts for diffusion of the concentrated force within the foundation

fcd = design value concrete compressive strength = αcc * fck / ɣc

αcc = coefficient for long term effects

fck = concrete characteristic cylinder strength

ɣc = partial safety factor for concrete

Note that even where a concrete foundation is not modeled, the coefficient, α, is calculated from the concrete dimensions shown in the base plate properties. The plan dimensions of the concrete foundation must be larger than the base plate (plus an allowance for grout), and the depth of the concrete foundation must be larger than the embedded bolt length plus an allowance for bottom cover.

Welds

Weld resistance varies by section type and whether direct contact in bearing is flagged on or off in the base plate properties - when on, axial force on the weld is taken as zero.

  • For I/H sections, flange welds resist the vector sum of axial force and minor shear force, while web welds resist major shear force. Forces and resistances are given in Force units.

  • For RHS sections, flange welds (faces A & C) resist axial force, while web welds (faces B & D) resist major shear force. Forces and resistances are given in Force units.

  • For CHS and SHS sections, an all around full profile weld resists the vector sum of axial force, major shear force and minor shear force. Forces and resistances are given in Force per length units.

Analysis

Connection forces are established from a global analysis of the building as a whole. Column base plates in Tekla Structural Designer have a limited set of design forces for which they can be designed. Non-design forces are identified and, where their value is greater than a given limit, they are displayed to you in the results along with a Warning status. The given limits are defined on the Design Forces page of the Design Settings dialog available from the Design tab on the ribbon.

The forces from the global analysis are treated in the following manner:

  • Simple column bases are designed for the positive axial force at the base of the column, the major shear (foundation reaction) in the plane of the column web (column section minor axis), and minor shear (foundation reaction) in the plane of the column flanges (column section major axis). Bases are orientated to the column’s major and minor axes and hence there is no requirement to resolve the force when the column is rotated. Columns can only be sloped in the plane of the web and the bottom stack axial force and shear are resolved into vertical and horizontal forces in the base.

Where the global analysis includes second-order (P-Delta) effects the Ultimate Limit State design forces will include these effects also. However, for column bases the design forces for soil bearing pressure calculations are taken from an elastic global analysis of the unfactored loadcases without second-order effects. Nevertheless, EQU and GEO load combinations are not considered in the base plate design i.e. these combinations do not appear in the results. All seismic (SEIS) combinations appear in the results. However, those deriving from ELF are considered for design while those from RSA result in Beyond Scope status.

Sign Conventions

The following sign conventions apply.

Convention looking at the column with face A on the right:

  • Positive major shear from face C to A,
  • Positive minor shear from face D to B,
  • Positive axial into the base.
Note: The column member direction arrow is placed on face A.