For some of the longitudinal reinforcement design parameters, additional user defined limits can be applied - where this is the case minimum and maximum values are specified in Design Options > Column > Reinforcement Layout.

Minimum Longitudinal Bar Spacing

For design to ACI ;

minimum clear distance
MAX (1.5 * longitudinal db , 1.5in., 1.33*hagg) US units
minimum clear distance
MAX (1.5 * longitudinal db , 40mm, 1.33*hagg) metric units
where
d b
  =  
bar diameter
h agg
  =  
aggregate size

Maximum Longitudinal Bar Spacing

You are given control over this value by specifying an upper limit in Design Options > Column > Reinforcement Layout.

Minimum Longitudinal Total Steel Area

For design to ACI;

1% * column area

Maximum Longitudinal Total Steel Area

For design to ACI;

8% * column area